I've done this twice & never had any issues. I did it this way because I've never had the main panel inside the garage.

Ran 10/3 from the main panel to a sub panel in the garage on a 70 amp breaker. The sub panel is set up for the welders & air compressor each on its own 30 amp breaker.

You could get away with just a 30 amp on the main panel with 10/3 to an outlet in your garage. I only did it my way for easy maintenance if it's required.

Often times the machine will stop itself before the breaker does. But if the manufacturer suggests a 40 amp then I'd go with that.

View attachment 526451

The problem with having #10 wire on a 70 amp breaker is now the wire becomes the fuse. I understand down stream you have 30 a breakers but still not proper protection for wire in use
 
The problem with having #10 wire on a 70 amp breaker is now the wire becomes the fuse. I understand down stream you have 30 a breakers but still not proper protection for wire in use

That's true & I may have misremembered. I'll check when I get home to make sure.

Edit: I was wrong, it's a 60 amp breaker.
 
Last edited:
I got to this point before having to quit for the nuggets game

20240516_183226.jpg
 
That's true & I may have misremembered. I'll check when I get home to make sure.

Edit: I was wrong, it's a 60 amp breaker.

I checked the breaker & it's a 60 amp, then I remembered why I set it up this way. This is a lot so bear with me.

The 60 amp breaker on the main panel feeds a 100 amp sub panel through 10/3 wire. I went with 100 amp only because I needed the 8 slots & this was readily available. 2 single pole 20 amp breakers for the lights, garage door openers, outlets & fans. Then 2 double pole 30 amp breakers for my air compressor & welder.

None of these things are constantly drawing power. I'm really only using 30 amps at a time if that. On the off chance that the air compressor kicks on (typically lasts about 30sec) while I'm welding, the 60 amp won't trip. The 10/3 can handle it only for a very short amount of time & that rarely occurs.

If I was constantly drawing the full 60 or 100 amps through the 10/3 wire then yes it would definitely fail.

Edit: I just realized I replied to my own message :rolleyes:
 
If anyone is interested, here's my setup for welding. I got some 10 ga extension cord wire from my Dad & hard wired the wall junction box to a junction box on my welding cart which splits into 2 outlets, one for each machine.
1000004085.jpg

The welding cart is from a Lincoln Power Wave that my last employer was throwing out which I modified to hold 4 bottles. I used some Lincoln wire spools to store all the hoses, leads, torches, etc. Another company I worked for laser cut a bunch of bottle hooks & I had asked for 4 sets of there were extras. I made some tungsten and Tig rod canister holders from some aluminum drops. I added the front handle & a bunch of other little things from scrap parts I found over the years.